I read the FAQ and it stated that You don't need a Smartshunt as well. This is probably fine if You're using an inverter or anything else that causes a permament load of over ~0.4 A.
I am building a 4S battery for my boat (EVE 280Ah), and the testrig I have right now (MPPT, JK-BMS, raspberry, smartshunt) draws around 5 watts all the time while idling as measured by the Smartshunt. The BMS says 0 A and Idle. It turns out that the JK BMS is unable to measure currents under 0.4 A or thereabout.
If you have a scenario with a small constant DC-load and you set the BMS as the battery monitor in a Victron GX device you will have issues with determining the correct SOC. Actually, You will believe You have a high SOC but you can be at 10% or less.
I feel that the Smartshunt calculates it correctly, after two weeks I have ~59% reported by the smartshunt and 82% by the BMS. I have manually drawn around 20 % from the battery after charging to avoid having it at high voltage, and the BMS hasn't moved a bit in two weeks despite a constant 5 W load.
TL;DR the battery with monitoring will empty itself in 30 days just by monitoring it. If you want to have a LiFePO₄ battery and not using it I recommend setting the sleep function on in the BMS and shutting if off.
(5 watts is ridiculous in itself, my ~65 liter fridge uses around 0.55 A in average during the day so the battery in itself with solar charger and monitoring draws almost as much as keeping a lot of beer cold)
reacted with thumbs up emoji reacted with thumbs down emoji reacted with laugh emoji reacted with hooray emoji reacted with confused emoji reacted with heart emoji reacted with rocket emoji reacted with eyes emoji
-
I read the FAQ and it stated that You don't need a Smartshunt as well. This is probably fine if You're using an inverter or anything else that causes a permament load of over ~0.4 A.
I am building a 4S battery for my boat (EVE 280Ah), and the testrig I have right now (MPPT, JK-BMS, raspberry, smartshunt) draws around 5 watts all the time while idling as measured by the Smartshunt. The BMS says 0 A and Idle. It turns out that the JK BMS is unable to measure currents under 0.4 A or thereabout.
If you have a scenario with a small constant DC-load and you set the BMS as the battery monitor in a Victron GX device you will have issues with determining the correct SOC. Actually, You will believe You have a high SOC but you can be at 10% or less.
I feel that the Smartshunt calculates it correctly, after two weeks I have ~59% reported by the smartshunt and 82% by the BMS. I have manually drawn around 20 % from the battery after charging to avoid having it at high voltage, and the BMS hasn't moved a bit in two weeks despite a constant 5 W load.
TL;DR the battery with monitoring will empty itself in 30 days just by monitoring it. If you want to have a LiFePO₄ battery and not using it I recommend setting the sleep function on in the BMS and shutting if off.
(5 watts is ridiculous in itself, my ~65 liter fridge uses around 0.55 A in average during the day so the battery in itself with solar charger and monitoring draws almost as much as keeping a lot of beer cold)